adccommunitymod (AutomationDirect) asked a question.

Allen Bradley 1734-AENT Point I/O (Remote I/O) with BRX PLC using Ethernet I/P

Created Date: September 30,2019

Created By: carnsdorff

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Is it possible to use Allen Bradley 1734-AENT Point I/O (Remote I/O) with BRX PLC using Ethernet I/P? I spoke with AD and they indicated it should be possible. However, I looked in the BRX software (Do-More Designer) and I didn't see how to configure it to communicate with the remote I/O. Any help would be useful - even if it is to tell me it isn't possible.


  • adccommunitymod (AutomationDirect)

    Created Date: September 30,2019

    Created by: carnsdorff

    Is it possible to use Allen Bradley 1734-AENT Point I/O (Remote I/O) with BRX PLC using Ethernet I/P?

    I spoke with AD and they indicated it should be possible.

    However, I looked in the BRX software (Do-More Designer) and I didn't see how to configure it to communicate with the remote I/O.

    Any help would be useful - even if it is to tell me it isn't possible.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: September 30,2019

    Created by: franji1

    BRX currently implements Explicit Message, but not I/O Scanner. Can your A/B 1734 be an Explicit Message Server? If so, then you can use BRX as an Explicit Message Client. However, if the A/B can only be an I/O Adapter, then BRX currently does not have the capability of being an I/O Scanner.

    Current plans are to add support for I/O Scanner in the next release.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 01,2019

    Created by: carnsdorff

    The 1734-AENT indicates it uses CIP messaging which I understand is explicit messaging.

    I 've been looking at how to do this but I 've never used this communications option.

    Any help on how to do this would be useful.

    I see how to set the BRX as an Ethernet I/P server, however, I was thinking it would be the client.

    I have the A/B manual discussing assembly instance, configuration size, etc. but I'm not sure how to use these.

    I see there is an EIPMSG block that is likely used for this but once again, it's all new to me.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 01,2019

    Created by: BobO

    Use EIPMSG instruction for client. EIP server is configured in the system configuration dialog.

  • adccommunitymod (AutomationDirect)

    Created Date: October 01,2019

    Created by: carnsdorff

    Thanks for the help!

    I'm still not sure how to configure the BRX plc to communicate with the AB point I/O.

    Are there any examples of setting up the BRX in a manner that would communicate with the remote AB point I/O?

    I don't see how to use the BRX to address the CIP parameters for the point I/O.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 02,2019

    Created by: carnsdorff

    I have the BRX PLC working with the example available from the AD video which uses the PLC as the server and the simulator as the client.

    The issue now is how to configure the IO.

    i don’t see the values to use which correspond to the EIPMSG items.

  • adccommunitymod (AutomationDirect)

    Created Date: October 02,2019

    Created by: z28z34man

    The 1734-AENT indicates it uses CIP messaging which I understand is explicit messaging.

    I 've been looking at how to do this but I 've never used this communications option.

    Any help on how to do this would be useful.

    I see how to set the BRX as an Ethernet I/P server, however, I was thinking it would be the client.

    I have the A/B manual discussing assembly instance, configuration size, etc. but I'm not sure how to use these.

    I see there is an EIPMSG block that is likely used for this but once again, it's all new to me.

    I am almost sure the 1734-AENT is implicit messaging. When setting up communication in the logix platform you need to set an RPI which indicates implicit to me. Explicit messaging is done through ladder logic and the PLC needs to ask the server every time.

    https://library.automationdirect.com/ethernetip-implicit-vs-explicit-messaging/

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 02,2019

    Created by: carnsdorff

    I'm not sure. The manual indicates explicit messaging but does indicate using a RPI.

  • adccommunitymod (AutomationDirect)

    Created Date: October 02,2019

    Created by: BobO

    Implicit capable devices often also support explicit. RPI would only apply to implicit. Data rate for explicit is defined in the EIPMSG instruction.

  • adccommunitymod (AutomationDirect)

    Created Date: October 03,2019

    Created by: carnsdorff

    How do I find the appropriate values to send for configuration and transfer of I/O information for the A/B point I/O using the EIPMSG?