• ADC Community_02 (Automationdirect.com)

    You can save recipes to a USB drive or SD card from the system setup screen. To get to the system setup screen, touch the top left corner of the touchscreen as shown at the following link

     

    https://cdn.automationdirect.com/static/manuals/ea9userm/ch5.pdf#page=13

     

    When the setup screen is called, press OK

     

    Once at the setup screen, select Memory, then select Backup. Choose your save device and press Next. Select Recipe and press Next. Follow the wizard to complete the backup. 

     

    To load the backup recipes onto a new panel, follow the same procedure except instead of Backup, you will now select Restore at the Memory screen. The link posted above discusses this in more detail.

    Expand Post
    • edgar (Customer)

      this is for backup the recipes

      i looking to have the actual recipes in usb so when i make changes i dont affect the saved recipes

      • ADC Community_02 (Automationdirect.com)

        Stored recipes on USB can not be directly accessed by the recipe objects. Only method is backup and restoring of recipes. Please clarify if I am not understanding correctly by providing more additional details on the process and/or steps you would like to accomplish.

      • edgar (Customer)

        maintenance can save the recipe, the problem is when we modify the applicaiton before we do it we need to upload the hmi then modify the application then download, this is becouse the recipe not save in different location