• alexmortenson (Customer)

    nodered 

    I tried to install this flow. It appears i need to upgrade things for this to work. This is the same issue with every module i tried to install.

    Expand Post
  • ADC_Click_PE01 (AutomationDirect)

    The C2-NRED is an embedded version and cannot be updated by customers. From the log you shared you are getting the CERT-NOT-YET-VALID error which means mostly likely your PLC and C2-NRED Clocks are not synced. Please see the CLICK User Manual page 5-22 for resolution to this error.