
EricCoplan (Customer) asked a question.
Stellar Soft Start SR55 100 HP
My facility has a 100 HP 124A rated softstart powering a lightly loaded 50 HP motor. The motor is pulling 24 amps at the most. Sometime it pulls less amps.
I am getting 403 Motor Side Phase Loss. I have double checked the disconnect and the motor connections. The motor meggs fine. The amps are 24 on all 3 phases. The coil to coil ohms on the motor are good. Everything looks fine.
From my research the SS is looking at the AMPS and if its below a threshold it will trigger a phase loss alarm.
Is there a way to lower the set point to account for a smaller motor?
You can shut the option off.
Sensitivity, 8.0 and Shear Pin 8.2 may help
NOTE: I have no personal experience with this SS