GSK72 (Customer) asked a question.
Hi, I was wondering, I am working on a project that has an electric heater that I want to know the heat output of it. I got this power meter, and I did not realize that it cannot do delta configuration. I just want to see if someone could provide give some insight to a thought of mine. From my understanding, the current, voltage and power factor should not be affected by the configuration as that is purely dependent on what the voltage and current measurements are on each leg of the 3P. After that, the only thing that changes are the power equations. Can someone confirm if I have the correct understanding.
Thanks!
I see. Thank you. Well, you could still use this to measure a line current and a L-L voltage and use the formula watts=line-to-line volts x line amps x sq root-3, and make those above assumptions. If used for relative heater power, and don't need point-of-sale-type absolute accuracy, this should work. Interesting, you must have an old electrical system that you have 480V delta. Is this corner-grounded? or mid-grounded? Floating? I've seen this in like 50's era buildings. Newer systems are 277/480 V, "Y", with the neutral grounded, and they use the 277V (Line-neutral) for 277V lighting.