Keystone Shawn (Customer) asked a question.
I'm using a EA3-T4CL HMI to act as a remote display/adjustment for a SOLO temperature controller using RS-485. The first machine I did this on, it worked perfectly. This is a picture of a test I did before hard mounting the display.
The production supervisor asked me to duplicate the effort on a second machine. It works, but I'm seeing various errors display across the top of the HMI.
"P007: CRC Not Match"
"P008: Address NotMatch"
"P009: Re. INV.FUN.Code"
"P499: Recv.ErrCode0009"
I believe this is because the second machine has a small pc board style PLC that is also on the RS-485 network. It is also connected to the SOLO and is displaying/adjusting the setpoint data on another HMI (via RS232) located on the opposite side of the machine. The first machine only had the SOLO temp. controller and the EA3 HMI.
Because the data being displayed is correct, I'm not concerned about the errors and I think they can be ignored. Is there a way to suppress them? I was not able to find anything in the C-more micro software about doing this.
There is no way to suppress these.
P007,008 and 009 are errors reported by the HMI, P499 is the HMI reporting an error it received from the Solo. P499 009 is a Checksum error. All of the errors point to a malformed packet.
Some suggestions:
1) Momentarily disconnection the PC from the RS-485 network and see if the PC really the cause. If the errors go away, check the echo suppression setting in the Micro and in the PC. In the C-more Micro project this is done by selecting RS-485 = Yes in the Panel Manager.
2) If the errors do not go away when you disconnect the PC, they are coming from somewhere else. I would suspect noise is getting on the RS-485 pair scrambling the packets. Is the cable shielded and grounded? Is it tie wrapped to a power cable or running in the same tray as a power cable? Try pulling it away from all other cables and see if the errors go away. That will tell you something. Try keying a radio in front of the cabinet. (Make sure nothing is running for safety reasons) If it causes errors, then you may have a shielding/grounding problem.
Thanks for the info. I tried disconnecting the PLC board from the RS-485. The red/black wires go to the EA3 and the white/green are for the existing PLC board.
In the C-more micro software, I already have "Select RS-485" set to Yes.
It loos like you have the PC wires also with that power wires also. If I am seeing that correctly that may be where the noise is coming in. I'd unbundle everything and keep the PC connected and see what happens.
Does the PC RS-485 cable have a shielded cable that is grounded on one end?
Also, make sure the Micro has a good ground. You are depending on that to drain the shield on the cable.
Hi @Keystone Shawn (Customer)
So the errors are caused by the other Master (PC) communicating to the Solo at the same time as the C-More Micro Master on the network.
This is not recommended for Modbus RTU. There should only be one master and several slaves on the same network.
You could try to change your poll time on the C-More. Hopefully, you can get lucky and pick a frequency that does not match the other PC.
You could replace the other Master (PC) with another C-More and Small PLC like a Click. The two C-More Microcontrollers communicating Ethernet to the Click. The Click would then communicate Modbus RS485 to the Solo.
Just a thought.
Regards,
Garry
https://accautomation.ca/click-plc-send-and-receive-instructions/
https://accautomation.ca/series/click-plc/
https://accautomation.ca/series/c-more-micro-hmi/
Good point Garry, I should have caught that. Can't have two masters on Modbus RTU and C-more is always the Modbus master.
Hi Gary. Thank you for your reply. Yeah, that's what I was afraid of.
A little background... The reason the first machine I did this on didn't have the pc board on the RS-485 is because that machine's HMI died. The board is still running some basic I/O functions on the machine, but since it could no longer display the temperature and allow for setpoint changes, I removed that wiring when I added in the c-more. It was also communicating on the RS-485 with a Yaskawa VFD to allow for speed changes, but I put in a pot. to handle that as a temporary measure.
So I guess the next step is replacing that pc board on the first machine, then when that's all working I can duplicate the results on the 2nd machine. BTW, I've used a few Clicks here already and really like them. I've been dragging my feet on this because the cabinet in the first machine is an absolute mess.
That is quite a feat to figured all that out and add a C-more Micro and get it all working. Yep, that's a mess.
Hi @Keystone Shawn (Customer)
No problem. I'm glad you got a plan going forward.
Let me know if you have any questions.
Regards,
Garry
P.S. This is a mess.
On the good side, those old-school Cutler-Hammer Citation series contactors should last forever. I have some in the field with 10s of millions cycles on them!