Wiring DC actuator with 750-2c relay

I'm DIY playing around with a used 24vdc 2-wire actuator that I'm looking to be able to drive in both directions. I've got an old AutomationDirect 750-2c DPDT octal relay that I believe should be able to use, however I don't know how to properly wire it up to achieve this. Anybody able to give me some guidance?

 

Relay Base

https://www.automationdirect.com/adc/shopping/catalog/relays_-z-_timers/relay_-a-_timer_sockets/750-2c-skt

 

Relay

https://www.automationdirect.com/adc/shopping/catalog/relays_-z-_timers/electro-mechanical_relays/750r-2c-24d

 

Actuator I'm using

https://ciar.it/catalog/en/linear-actuator-kits/59-lm55-05.html


  • OkiePC (Customer)

    Your single relay gives you two states for your motor wiring and you need three:

    1) Stopped

    2) Run FWD

    3) Run REV

    You need a minimum of two relays.

     

    Typically, you will reverse the polarity going to a DC motor to reverse direction of travel, so your relay wiring would look something like what is described here and I agree with Bernie's recommendation of 3 pole relays so you can interlock them to reduce possibility of a short circuit.

    https://www.plctalk.net/threads/dc-motor-control.20148/#post-138494

     

    Expand Post
  • Nebr. Tech (Customer)

    Here's a wiring diagram of one way to do it.Actuator direction control

  • OkiePC (Customer)

    And since it is a linear actuator, I would add in some over travel limit switches to the circuit.

  • InsaneGeek (Customer)

    Thanks for the responses, I believe I've figured out the correct wiring to switch polarity, I have a second relay for power control. For future reference if any one has a similar question this is what I came up with

     

    750-2C-SKT Polarity Reverse 

    750-2C-SKT

    Expand Post