BreadGuyJeff (Customer) asked a question.
I am using the P1-550 and a P1-RX remote IO unit and I am having a great deal of difficulty connecting my programming laptop to the PLC through the Ethernet port. It does work sometimes but it is very slow, like the PLC isn't discovered in the Choose CPU tab until after several refreshes and once I connect a the Clock Seconds register only updates about once every five or ten seconds. The computer is directly connected to the PLC Ethernet port with nothing else on the network and I have tried multiple Ethernet cables.
This is my first time using the remote IO and I am wondering if that slows down the Ethernet port? I use another P1-550 in another application and it's connection is lightning fast. Also I pinged the IP from my windows cmd prompt and it was less than 1 ms. And roundtrip is reported as 0 ms.
Bad hardware, but my fault!
I found my RJ45 connector I crimped on had 2 pins that did not crimp fully(strange how this happened as I used a quality Klein crimping tool but I will inspect this more carefully in the future). One of these pins caused the female port on the PLC to have a pin get bent down and stuck. It is strange it worked at all but basically when pinging it I would get fast responses but about every third or fourth packet was dropped.