markshancock (Customer) asked a question.
We have a PLC program that in one part, forwards modbus commands to another controller.
See the screen shot below. Note in rung 2 and 4 C70 is showing as both rising and falling at the same time. I can't see how that should be possible.
The blue is to illustrate the status of the C70 address, meaning it's true. What it does not show is the actual status of the one-shot instructions. This is because one-shot rising - or falling - happen in one scan, so an attempt to show this would be almost futile.